The question concerns whether a building fed by two different services should have their grounding systems tied together to minimize potential differences between grounded equipment.Here's the background. This is for a school campus. What do you think? THE CAMPUS HAS 7 BUILDINGS. THERE ARE TWO SEPARATE SERVICES WITH INDIVIDUAL METERING, ONE IS FOR 120/208v AND ANOTHER FOR 460V. BOTH SERVICES ARE LOCATED AT DIFFERENT BUILDINGS WITH TWO SEPARATE UTILITY CONNECTION POINTS AT THE STREET. THE 120/208 SERVICE HAS RECENTLY BEEN UPGRADED ON EACH BUILDING AND A GROUNDING ELECTRODE SYSTEM ( GROUND ROD & WATER PIPE CONNECTION) HAS BEEN INSTALLED.
EACH BUILDING ALSO INCLUDES A 460VOLT SERVICE FOR AIR CONDITION EQUIPMENT THAT DOES NOT HAVE A GROUNDING ELECTRODE SYSTEM ATTACHED TO IT.
AFTER MUCH DISCUSSION, I WAS TOLD BY MY FACILITIES DEPT THAT YOU CANNOT CONNECT GROUNDING SYSTEMS OF THESE TWO SERVICES TOGETHER. ONE REASON WAS THAT IT WAS AN UTILITY VIOLATION. ANOTHER WAS THAT IT WILL CREATE A GROUND LOOP. AS PER THE "NEC", YOU MUST PROVIDE A GROUNDING ELECTRODE SYSTEM FOR ANY BUILDING SERVICE (WITH THE EXCEPTION OF A SINGLE CIRCUIT) AND IF ANOTHER SERVICE EXISTS ON THIS BUILDING, YOU MUST ALSO CONNECT TO THE SAME GROUNDING ELECTRODE SYSTEM THEREBY EFFECTIVELY BONDING THE TWO SERVICES TOGETHER. AS IT IS NOW, THERE CAN BE A POSSIBLE POTENTIAL DIFFERENCE BETWEEN GROUNDED EQUIPMENT OF BOTH SERVICES. I FEEL THAT THIS A VERY UNSAFE CONDITION.
EACH BUILDING ALSO INCLUDES A 460VOLT SERVICE FOR AIR CONDITION EQUIPMENT THAT DOES NOT HAVE A GROUNDING ELECTRODE SYSTEM ATTACHED TO IT.
AFTER MUCH DISCUSSION, I WAS TOLD BY MY FACILITIES DEPT THAT YOU CANNOT CONNECT GROUNDING SYSTEMS OF THESE TWO SERVICES TOGETHER. ONE REASON WAS THAT IT WAS AN UTILITY VIOLATION. ANOTHER WAS THAT IT WILL CREATE A GROUND LOOP. AS PER THE "NEC", YOU MUST PROVIDE A GROUNDING ELECTRODE SYSTEM FOR ANY BUILDING SERVICE (WITH THE EXCEPTION OF A SINGLE CIRCUIT) AND IF ANOTHER SERVICE EXISTS ON THIS BUILDING, YOU MUST ALSO CONNECT TO THE SAME GROUNDING ELECTRODE SYSTEM THEREBY EFFECTIVELY BONDING THE TWO SERVICES TOGETHER. AS IT IS NOW, THERE CAN BE A POSSIBLE POTENTIAL DIFFERENCE BETWEEN GROUNDED EQUIPMENT OF BOTH SERVICES. I FEEL THAT THIS A VERY UNSAFE CONDITION.