I am designing the electrical system for a building addition at a high school. The new addition will be attached to the existing building, separated by fire walls.
A new electrical service with new utility transformer will be installed approximately 400' from the existing utility transformer and service.
There was a request from the owner to provide a ground from the new data/telecom room to the existing data/telecom room. I was working on my details sheet and came up with the following question....
The new service would normally include a ground wire to a ground bar in the new data/telecom room. Do I not do this and ground the new bar in the new room to the existing room per the owners request?
Which leads me to my next question...do I need to ground the two services together? There will be a new water service for the building additions well.
New grounding system will consist of ground rods. The grounding system used by the existing building is unknown.
A new electrical service with new utility transformer will be installed approximately 400' from the existing utility transformer and service.
There was a request from the owner to provide a ground from the new data/telecom room to the existing data/telecom room. I was working on my details sheet and came up with the following question....
The new service would normally include a ground wire to a ground bar in the new data/telecom room. Do I not do this and ground the new bar in the new room to the existing room per the owners request?
Which leads me to my next question...do I need to ground the two services together? There will be a new water service for the building additions well.
New grounding system will consist of ground rods. The grounding system used by the existing building is unknown.