In a sub panel I see were there is a metal bar that runs across from the grounding side to the neutral side, this bar needs to be remove as my under standing, is this correct?:?
Panel is after first means of diconnectIn a sub panel I see were there is a metal bar that runs across from the grounding side to the neutral side, this bar needs to be remove as my under standing, is this correct?:?
Panel is after first means of diconnect
I mean is the subpanel in a detached / separate building of structure from the first means of disconnect?
Drawing a simple wiring diagram may clarify it.
At me end draw a device entrance with the N and EGC connected together. The draw two parallel lines connecting them together at the farther end. Now visualize a line to neutral load when the neutral current is now shared by the EGC.
If the neutral is grounded at the SE of then somewhere down the line you bond the neutral to the EGC again then you have provided a path for the neutral current to travel a parallel path back to the SE. Consider that grounding prong in a grounded tool or appliance that plugs into the EGC. Would it be a good idea to have a neutral current using the EGC to return to the SE? I think not and it provided and opportunity for an electric shock should you come into contact with the tool or appliance.
Bottom line? You certainly don't want any neutral current to use the EGC as a return path to the SE.
Yes, I see now as it is only highly restricted conditions such as:Bottom line, code wise, safety wise if the OPs subpanel is at a separate building or structure it may be necessary to leave the neutral bonded to the EGCs.
We don't yet have enough info to recommend lifting this bond.
Since you are adding a ground bar which is screwed directly to the panel have you addressed that bonding screw that is still present that is still bonding the now neutral bar to the box?Don't remove the bar between the two. Just add a ground bar with more than the necessary number of terminals for the grounds. Then move all the grounds there, make sure it's bonded to the box and the egc coming from the feeder.
Since you are adding a ground bar which is screwed directly to the panel have you addressed that bonding screw that is still present that is still bonding the now neutral bar to the box?
And the beat goes on, let's all take a guess and what the OP has. He"miight be" etc. It bothers me that quite often it appears as though we are handing someone a loaded gun. It would be interesting to know if a panel is offered with an neutral bar with no bonding scew installed of provided for bonding. I would like to think that there was but without being specific kit is to be questioned.We don't know if there's a bonding screw, actually. OP hasn't told us as much. Frankly, the use of "neutral side and ground side" leads me to believe OP just thinks that the neutral bar on the left is different than the neutral bar on the right. And also OP leads me to believe he might be installing this new, in which case the bonding screw/strap or whatever hasn't even been installed yet.
It would be interesting to know if a panel is offered with an neutral bar with no bonding scew installed of provided for bonding. I would like to think that there was but without being specific kit is to be questioned.
Oh well.
That is not always so. Cutler Hammer BR has a neutral bar that runs behind the buss but it is isolated unless you bond it to the can.First off, does that metal bar between the neutral strips happen to run behind the buss bar assembly?
If so, it is mechanically attached to the panel enclosure which makes this panel "suitable only as service equipment"....
That is not always so. Cutler Hammer BR has a neutral bar that runs behind the buss but it is isolated unless you bond it to the can.