tom.bielectric
Member
- Location
- Pennsylvania, USA
New to the forum, hope you can help with my confusion regarding grounding & neutral connections: We installed a 2000A switchgear 480/277V 3 phase in a small building. That is our main service, grounds & neutrals are bonded together there. In that small building we also have a 75KVA transformer (3phase 120/208 secondary). We have the grounds and neutrals connected together at the transformer. That transformer feeds a 3 ph panel. Should the ground & neutrals be together or separate in that panel? To complicate things, there is a larger building that is fed from the switchgear.... 800A, 480/277 main breaker panel. The inspector said he wants the ground and neutrals separated in that panel. Then from that 800A panel, we have several transformers that feed sub panels. How should the ground/neutral connections be in the transformers, and panels? We tried to keep them separate in the transformers in that larger building, but got screwy voltage readings... then bonded them together at the transformers, and all readings are now OK. Can you give any advice? Thank you.