I would like to confirm whether the following grounding scenario is confirmed in the NEC. I could not find it when I read the NEC handbook:
I have a 12,4000/7,200X208/120v Wye-Wye connected 300KVA transformer that is has the following items connected to the transformer ground ring: Cable Shields, Chassis Ground, Surge Arrestor. The secondary neutral is connected to a separage ground rod a minimum of 6000mm from the ground rod per this installation practice that has been suggested to me in the referenced drawing.
What would the reason be for connecting the secondary neutal to a separate ground rod separate from the ground ring of the transformer since it is apparently not covered by the NEC.
I have a 12,4000/7,200X208/120v Wye-Wye connected 300KVA transformer that is has the following items connected to the transformer ground ring: Cable Shields, Chassis Ground, Surge Arrestor. The secondary neutral is connected to a separage ground rod a minimum of 6000mm from the ground rod per this installation practice that has been suggested to me in the referenced drawing.