The NEC never requires more that two ground rods. There is no requirement for a ground ring (loop) or test wells. If a ground ring is used, there is no NEC requirement to have any ground rods. If you choose to install a ground ring, the minimum wire size for the ground ring wire is #2.I need help with developing a grounding plan for a warehouse. Is there a NEC code where it talks about the spacing between the grounding rods around the building, ground test wells, ground loop conductor size, bonding the equipment etc?
Thanks!
Thanks!! I wonder if we need to install ground rod every 20' and ground every other columns?
Not sure what the lightning protection code (NFPA 780) may require, but the NEC does not require that.Its a new distribution center I'm working on and I am doing the grounding plan. I believe if there is a lightning protection system, we need to run a down conductor and and then connects to the ground rod.
I was under the assumption that it is a best practice to install ground test wells at each corner of the building.
Also, I believe I have to bond every other steel columns and also bond the rebar to counterpoise.
Its a new distribution center I'm working on and I am doing the grounding plan. I believe if there is a lightning protection system, we need to run a down conductor and and then connects to the ground rod.
I was under the assumption that it is a best practice to install ground test wells at each corner of the building.
Also, I believe I have to bond every other steel columns and also bond the rebar to counterpoise.