Some time ago, I worked with someone in some work in a substation. In addition to MV breakers, shutting the system off involved operating a knife switch. One had to open it, then close another set of blades. This was to clear the residual voltage from the metal cable casing. When this happened, you could hear and see a little bit of spark.
More recently, I have worked with some wye connected transformers, where this was not a requirement. The casing was grounded to the frame, so it is not live when the power is removed.
I never understood the difference in the systems and why we had to have it in the substation.
I currently am involved with a project with two transformers (one to step up and the other to step down) that have a 12.47 kV delta on the HV side. I am wondering if this scenario requires something like the substation I mentioned. Does one ground the concentric neutral or tape shield of the MV wire to earth in this case, or must it be isolated and then grounded when the circuit is opened? If the letter, how is this commonly done with a transformer that has integral load break switch?
More recently, I have worked with some wye connected transformers, where this was not a requirement. The casing was grounded to the frame, so it is not live when the power is removed.
I never understood the difference in the systems and why we had to have it in the substation.
I currently am involved with a project with two transformers (one to step up and the other to step down) that have a 12.47 kV delta on the HV side. I am wondering if this scenario requires something like the substation I mentioned. Does one ground the concentric neutral or tape shield of the MV wire to earth in this case, or must it be isolated and then grounded when the circuit is opened? If the letter, how is this commonly done with a transformer that has integral load break switch?