Grounding of grouped disconnects remote to building

Status
Not open for further replies.

JoeNorm

Senior Member
Location
WA
I am not getting any responses in the grounding and bonding section so I am going to ask again here.

I am trying to understand the GEC requirements for a grouping of disconnects next to a transformer at the street, each 200 amp disconnect feeds a residence.

It appears I can have one common GEC and tap off of it to get to all the enclosures. Am I seeing it correctly that if 4/0 Al is the largest conductor then I need #4 copper as the primary GEC? I can then tap with #6 copper? It appears that split bolts can be used for the taps?

Another idea would be to run a GEC(#6 bare copper) from each enclosure back to the first ground rod, each with its own acorn. Would this be permissible?

Thanks for your time
 
Either method is permissible,
Note 250.64 (B)(2) in regard to the #6
 