Grounding of Main SwitchBoards

Status
Not open for further replies.

Samardas

Member
Location
Los Angeles, CA, United States
Occupation
Electrical Engineer
I am designing a system with two transformers coming out of one feeder manhole from the Utility company, one for a 2000A service and the other for a 1600A service. In the design I showed (5) 4"C (PVC-non metallic) with 4X600AWG and one (1) #3/0 Gnd. in each conduit for 2000A and (4) 4"C with 4x600AWG and one (1) #3/0 Gnd. in each for 1600A service. In the Main Switchboards, I showed Neutral and Ground Bus connected and then connected to the ground ring.

But the contractor says since they have a ground ring and a cold water pipe, which they are using for the transformer grounding, there is no need to run a #3/0 through each conduit as I had suggested. Instead they want to connect the MSBs' Neutral and Ground Bus to the same ground ring. When I look at the NEC (2013 and 2014), I get little confused as to what is acceptable. What are your thoughts? Diagram attached for your ref. Thanks a Lot for your help!!! (Although, I am trying to learn as fast as I can, perpetually I get confused when it comes to grounding:?)
 

Attachments

  • H St_SLD_E02_Mike Holt Forum_110615.pdf
    98.8 KB · Views: 4

wsbeih

Member
Location
USA
I am designing a system with two transformers coming out of one feeder manhole from the Utility company, one for a 2000A service and the other for a 1600A service. In the design I showed (5) 4"C (PVC-non metallic) with 4X600AWG and one (1) #3/0 Gnd. in each conduit for 2000A and (4) 4"C with 4x600AWG and one (1) #3/0 Gnd. in each for 1600A service. In the Main Switchboards, I showed Neutral and Ground Bus connected and then connected to the ground ring.

But the contractor says since they have a ground ring and a cold water pipe, which they are using for the transformer grounding, there is no need to run a #3/0 through each conduit as I had suggested. Instead they want to connect the MSBs' Neutral and Ground Bus to the same ground ring. When I look at the NEC (2013 and 2014), I get little confused as to what is acceptable. What are your thoughts? Diagram attached for your ref. Thanks a Lot for your help!!! (Although, I am trying to learn as fast as I can, perpetually I get confused when it comes to grounding:?)

You got a non metallic conduit. The way i see it you need to keep the #3/0 GND to comply with supply side bonding jumper NEC requirement.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If the conduits contain service entrance conductors you do not need an EGC in each raceway. Installing one would put the EGC's in parallel with the neutral which would create a parallel path for the neutral current and a violation of 250.6(A).
 

Samardas

Member
Location
Los Angeles, CA, United States
Occupation
Electrical Engineer
Grounding of Main SwitchBoards

So, what is the verdict? Should I use 1x3/0 grounding conductor through each conduit or ground the system separately to the same ground ring without using a separate 3/0 conductor in each conduit. Not quite clear from the NEC.
Thanks a LOT!
Samar
 