Samardas
Member
- Location
- Los Angeles, CA, United States
- Occupation
- Electrical Engineer
I am designing a system with two transformers coming out of one feeder manhole from the Utility company, one for a 2000A service and the other for a 1600A service. In the design I showed (5) 4"C (PVC-non metallic) with 4X600AWG and one (1) #3/0 Gnd. in each conduit for 2000A and (4) 4"C with 4x600AWG and one (1) #3/0 Gnd. in each for 1600A service. In the Main Switchboards, I showed Neutral and Ground Bus connected and then connected to the ground ring.
But the contractor says since they have a ground ring and a cold water pipe, which they are using for the transformer grounding, there is no need to run a #3/0 through each conduit as I had suggested. Instead they want to connect the MSBs' Neutral and Ground Bus to the same ground ring. When I look at the NEC (2013 and 2014), I get little confused as to what is acceptable. What are your thoughts? Diagram attached for your ref. Thanks a Lot for your help!!! (Although, I am trying to learn as fast as I can, perpetually I get confused when it comes to grounding:?)
But the contractor says since they have a ground ring and a cold water pipe, which they are using for the transformer grounding, there is no need to run a #3/0 through each conduit as I had suggested. Instead they want to connect the MSBs' Neutral and Ground Bus to the same ground ring. When I look at the NEC (2013 and 2014), I get little confused as to what is acceptable. What are your thoughts? Diagram attached for your ref. Thanks a Lot for your help!!! (Although, I am trying to learn as fast as I can, perpetually I get confused when it comes to grounding:?)