Does the electrode conductor (1/0) stranded copper need to be buried? Please read below.
Is this a safe and acceptable method of grounding?
These stations are normally 10-12'W by 20-30' L concrete pads. We bury the 1/0 in a 10 inch trench for protection of the wire and strap down what we might have running on top of the pad.
Installed are 8? ground rods (ref NEC article 250.52 (5), article 250.53 (A,B,C) that are driven in the ground and measured with a ground tester. If a high reading is present, then another rod is attached by cadweld and repeated until we have the acceptable reading. (Preferably 5 ohms per equipment manufacture and NEC article 250.6 requires 25 ohms) After an acceptable reading is achieved, it is then repeated for each ground rod. Each rod is spaced 8? apart from each other. Then a 1/0 conductor (NEC 250.62 and NEC 250.64) is used to connect the grounding electrodes to complete a grounding electrode system.
Is this a safe and acceptable method of grounding?
These stations are normally 10-12'W by 20-30' L concrete pads. We bury the 1/0 in a 10 inch trench for protection of the wire and strap down what we might have running on top of the pad.
Installed are 8? ground rods (ref NEC article 250.52 (5), article 250.53 (A,B,C) that are driven in the ground and measured with a ground tester. If a high reading is present, then another rod is attached by cadweld and repeated until we have the acceptable reading. (Preferably 5 ohms per equipment manufacture and NEC article 250.6 requires 25 ohms) After an acceptable reading is achieved, it is then repeated for each ground rod. Each rod is spaced 8? apart from each other. Then a 1/0 conductor (NEC 250.62 and NEC 250.64) is used to connect the grounding electrodes to complete a grounding electrode system.