typically i ground the pedestals of raised flooring, the reason i do this is usually the raised floor is in an ITT room, and in accordance with NEC 545.15 -- this is required.
but, what about in a room that is not an ITT room, no computer servers or racks, with a raised floor.
i think the pedestals still need to be grounded because of NEC 250. am i correct about this? there is no specific requirement called "raised flooring" in article 250.
please provide an NFPA or an NEC article that requires me to ground pedestals in a raised floor area that is not an ITT room
jcd
but, what about in a room that is not an ITT room, no computer servers or racks, with a raised floor.
i think the pedestals still need to be grounded because of NEC 250. am i correct about this? there is no specific requirement called "raised flooring" in article 250.
please provide an NFPA or an NEC article that requires me to ground pedestals in a raised floor area that is not an ITT room