donhawley
Member
- Location
- Pocahontas, IL 62275
We find 3 wire feeds to a remote (sub panel) from a service panel quite often in our area. The question is if a remote panel is fed by a 3 wire conductor (H H N) but no ground wire or metallic conduit connection to the grounded neutral in the service box, how do you configure the 12-w/g wiring for the load circuits. I understand the neutral must be isolated but I also believe the grounds and neutrals are not allowed to be connected together past the service box. Not connecting the grounds to the neutral would mean these circuits were not grounded. This would be old construction in the same building (ie basement, attached garage etc), how do you bring this up to current code. Could the sub panel be treated as a service panel with a new ground rod or must the ground come the service panel?