Been awhile since I have done any large service work, was kind of thrown into this job have some questions about the grounding for the service?. The service is parallel 300MCM with a #2 ground that goes to a CT cabinet. From the CT cabinet the 300MCM goes to a trough with a 1/0 ground. There are also 3 - 200 amp main breaker panels that feed into the trough each with a #4 ground. I have a 1/0 ground that comes from water service piping and a #6 going to the ground rods.
Am I correct that I just need to land all of the 1/0?s and #4?s together in the trough.? Do I need to bond the neutral for the CT cabinet with the #2 ground for the service. Does the #6 from the ground rods need to land in each of the 200amp panels, or where? Are bonding bushings required for the 3? conduits for the 300MCM. any assistance in this matter would be greatly appricated
Am I correct that I just need to land all of the 1/0?s and #4?s together in the trough.? Do I need to bond the neutral for the CT cabinet with the #2 ground for the service. Does the #6 from the ground rods need to land in each of the 200amp panels, or where? Are bonding bushings required for the 3? conduits for the 300MCM. any assistance in this matter would be greatly appricated