Just ran into a house that is not grounded properly.
The meter base is located on one end of the house and has a ground rod connected.
The original owner ran a 3 wire SE cable that is now unaccessable. (No EG)
Inside panel is located on the other end of the house with no grounding lugs. Only neutral bar where owner connected both feeder grounds and neutrals to it. The is no bond screw.
In order to correct should I install additional ground rod and grounding lugs and connect the two, then separate the feed neutral from EG. Or must I run a #4 bare ground around perimeter of house and connect to existing ground rod?
The meter base is located on one end of the house and has a ground rod connected.
The original owner ran a 3 wire SE cable that is now unaccessable. (No EG)
Inside panel is located on the other end of the house with no grounding lugs. Only neutral bar where owner connected both feeder grounds and neutrals to it. The is no bond screw.
In order to correct should I install additional ground rod and grounding lugs and connect the two, then separate the feed neutral from EG. Or must I run a #4 bare ground around perimeter of house and connect to existing ground rod?