Grounding Panels/ Distribution Boards

Status
Not open for further replies.

mstrlucky74

Senior Member
Location
NJ
If there are branch panelboards and distribution boards how do they achieve being grounding? By the feeders that feed them? Because(obviously) there are not separate conductors run to a ground bar) Only usually see details like this that ground the main service DIRECTLY to the main ground bar? Thanks
 

Attachments

  • Grounding Detail.jpg
    Grounding Detail.jpg
    13.1 KB · Views: 0

mstrlucky74

Senior Member
Location
NJ
Per below I'm not clear by the "ground bushings connected to ground bus by mean of cooper wire". There is never a separate ground wire that goes from a panel to a ground bar.

Equipment Ground detail: All conduits entering service or distribution switchboards, distribution or power panels,
[FONT=Arial,Arial Narrow][FONT=Arial,Arial Narrow]transformers, PDU’s, and ATS shall be provided with grounding bushings, connected to the respective equipment [/FONT][/FONT]
ground bus by means of an insulated copper wire (sized as per code requirements). All conduits entering cable
support boxes, pull boxes and junction boxes shall be provided with (2) grounding locknuts (1 inside 1 outside the enclosure). All non-[FONT=Arial,Arial Narrow][FONT=Arial,Arial Narrow]conductive paint or coating’ shall be removed from the enclosure at the threads, contact points [/FONT][/FONT]and contact surfaces unless the fitting provided is designed to make such removal unnecessary.
 

mstrlucky74

Senior Member
Location
NJ
Per below I'm not clear by the "ground bushings connected to ground bus by mean of cooper wire". There is never a separate ground wire that goes from a panel to a ground bar.

Equipment Ground detail: All conduits entering service or distribution switchboards, distribution or power panels,
transformers, PDU’s, and ATS shall be provided with grounding bushings, connected to the respective equipment
ground bus by means of an insulated copper wire (sized as per code requirements). All conduits entering cable
support boxes, pull boxes and junction boxes shall be provided with (2) grounding locknuts (1 inside 1 outside the enclosure). All non-conductive paint or coating’ shall be removed from the enclosure at the threads, contact points and contact surfaces unless the fitting provided is designed to make such removal unnecessary.

Mod can you move thread to the grounding section. TY
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Sounds like they want a bonding jumper from the conduit to the EGC bus via a wire.