Hi Folks,

I've ran into a situation with my local building official, and I would love some input on the subject matter.

Scenario:
400Amp service being fed by (2) Sets of (4-wire) 3/0 Cu.

Based off NEC 250.66 and the cross sectional area, should the ground be based on number of sets, thus (2) 3/0 Cu.

OR

Should it be based on total wires, thus (8) 3/0 Cu.

Any and all input would be appreciated.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
If you are asking about the grounding electrode conductor, it is based on the sum of the circular mil area of two 3/0 conductors. 167,800 x 2 = 335.6 kcmil requiring a 2 AWG copper grounding electrode conductor.
See Note 1 in Table 250.66.
 