When paralleling multiple generators I have seen installations where the N/Grd. connection is located in the output section of the generator terminal cabinet, in others I have seen where the N/Grd. connection is made at the parallel switchgear and at the generator the neutral and grounds are isolated with the grounds connected to the generator frame and the neutrals connected to the “T0” terminal. Is there an advantage to one vs. the other? In reading IEEE 446 [Orange Book] it indicates that this connection is “usually connected to a common neutral bus within the parallel switchgear”. But does not comment on connections at the generator for parallel operations. Is there an industry preference or advantage one vs the other?