Tim K
Member
- Location
- Southeastern PA
I know, I know. There are countless threads about grounding portable generators, but most of them are pretty specific to each scenario. I've read them all. I know there are plenty of opinions on the subject and I hope I can just get a few of them! This ties in with a post I made a few months ago, but that's locked now so I have to start a new thread I guess....
The house was built in the early 90's. There is a single grounding rod buried by the service entrance for the gas and electric. The main panel has a ground wire run to the rod outside, as well as a second ground wire clamped to a nearby water line (about 30ft after the meter). There is a jumper over the meter. Without digging up the front yard I can't be certain, but I'm pretty sure the water service is metal from the street.
The generator is setup to run on the back of the house because it is partially sheltered by a deck, and is also away from the neighbors to keep the peace. A power inlet box will be mounted on the wall and wired to the manual transfer switch located next to the panel. The transfer switch (Generac 6294) does NOT switch neutral. The generator is a 7000W/8500W portable generator. The generator came with the neutral bonded but the bond was removed as per the manufacturer's instructions.
By definition this would be a Non-SDS, and thus wouldn't require it's own grounding system, only that it be tied to the building's GES.... Correct?
A 30amp circuit calls for a 10ga ground wire (coated green), which would be run unbroken to a nearby copper cold water line.
All of this is shown in the attached graphic.
Are there any flaws in this setup? First, as far as grounding the generator to the building's GES.....is tying in to any part of the water line sufficient? I couldn't find anything in any codes that specified where the connection to the GES had to be made.
Obviously today's code requirements for grounding the main service would be different. I believe it would require at least one more grounding rod buried at least 6ft from the first, and also the ground wire from the main panel to the water service would have to be attached within 5ft of the service entrance. I don't think doing either is 'required' since this is all grandfathered in so-to-speak. But if it were your house, would you bother to drive another rod? Would you run a new ground wire from the panel the extra 30ft to the water service entrance?
Thanks for your input/insight.
-Tim
The house was built in the early 90's. There is a single grounding rod buried by the service entrance for the gas and electric. The main panel has a ground wire run to the rod outside, as well as a second ground wire clamped to a nearby water line (about 30ft after the meter). There is a jumper over the meter. Without digging up the front yard I can't be certain, but I'm pretty sure the water service is metal from the street.
The generator is setup to run on the back of the house because it is partially sheltered by a deck, and is also away from the neighbors to keep the peace. A power inlet box will be mounted on the wall and wired to the manual transfer switch located next to the panel. The transfer switch (Generac 6294) does NOT switch neutral. The generator is a 7000W/8500W portable generator. The generator came with the neutral bonded but the bond was removed as per the manufacturer's instructions.
By definition this would be a Non-SDS, and thus wouldn't require it's own grounding system, only that it be tied to the building's GES.... Correct?
A 30amp circuit calls for a 10ga ground wire (coated green), which would be run unbroken to a nearby copper cold water line.
All of this is shown in the attached graphic.
Are there any flaws in this setup? First, as far as grounding the generator to the building's GES.....is tying in to any part of the water line sufficient? I couldn't find anything in any codes that specified where the connection to the GES had to be made.
Obviously today's code requirements for grounding the main service would be different. I believe it would require at least one more grounding rod buried at least 6ft from the first, and also the ground wire from the main panel to the water service would have to be attached within 5ft of the service entrance. I don't think doing either is 'required' since this is all grandfathered in so-to-speak. But if it were your house, would you bother to drive another rod? Would you run a new ground wire from the panel the extra 30ft to the water service entrance?
Thanks for your input/insight.
-Tim