Grounding Problem

Status
Not open for further replies.

Basra123

Member
I have 25kva 120/240 service transformer. I measure 126 on each phase and 252 between the phases. When the transformer is connected to a sevice entrance there is a potential difference between the transformer's nuetral and the sevice entrance ground of 3 volts. This 3 volts cause arcing on the casing of the well, which is grounded, fed of this sevice. why there is 3 volt differce between the two grounds? How to get rid of this 3 volt differential ???
 
Re: Grounding Problem

Where in the distribution system is the separately derived system's (transformer secondary) neutral bonded to ground? Is there a grounding electrode conductor run from the XO of the transformer to the grounding electrode system?
 
Re: Grounding Problem

This 3 volts is the voltage drop on the service neutral. I doubt you have a real problem if all bonding and grounding is performed correctly at the transformer and at the service, save for possibly and undersized grounded conductor.
 
Re: Grounding Problem

Is the transformer a "service transformer or SDS?Where is the main or system bonding jumper? Where exactly are you placing the meter leads to read the 3 volts?
Don
 
Re: Grounding Problem

This 3 volts cause arcing on the casing of the well,
Arcing? sounds like there is something loose somewhere, have you checked all your connections, maybe a lug is stripped out and not tight.
 