Do pull boxes and troughs have to be grounded or bonded in a conduit run.
T transman2 Senior Member Location Brooklet,Ga. Jul 29, 2013 #1 Do pull boxes and troughs have to be grounded or bonded in a conduit run.
ptonsparky Tom Location NE (9.06 miles @5.9 Degrees from Winged Horses) Occupation EC - retired Jul 29, 2013 #2 Yes, raceway type, voltage, current rating of feeder protection, and specs will determine the details.
Yes, raceway type, voltage, current rating of feeder protection, and specs will determine the details.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Jul 29, 2013 #3 transman2 said: Do pull boxes and troughs have to be grounded or bonded in a conduit run. Click to expand... In many cases if you have a metallic conduit the raceway can ground the PB or trough.
transman2 said: Do pull boxes and troughs have to be grounded or bonded in a conduit run. Click to expand... In many cases if you have a metallic conduit the raceway can ground the PB or trough.
tom baker First Chief Moderator Staff member Location Bremerton, Washington Jul 30, 2013 #4 Yes and no for pull boxes. See 250.148 (a change from 2005 NEC) For a trough (this is not a code term) so you may be referring to a wireway, voltage and KO type dictates if bonding is required.
Yes and no for pull boxes. See 250.148 (a change from 2005 NEC) For a trough (this is not a code term) so you may be referring to a wireway, voltage and KO type dictates if bonding is required.