Grounding PV tracker

Merry Christmas

LuisValverde

New User
Location
México City
Occupation
Project Engineer
Hello

I have the following situation.

We need to ground the torque tube of a PV tracker, considering 690.31 Methods Permitted (E), cable used for this porpuse need at least 49 strands (we are using 6AWG), this is class G cable.

According to NEC 110.14 connectors and terminals must be identified for use with Class G. So I need a terminal ring lug and a clamp than are suitbale for fine stranded wire and also to be UL467 for grounding, I think this combination is not that common.

I'm looking for a catalog or alternative solutions.

Thanks
 