Here is the situation:
It looks like panelboard PP-2 was the original main service panelboard. At some later date an addition was built and PP-2 became a subpanel (with a new feeder) connected to PP-1 which is at the service. The feeder is in a RGS conduit underground to PP-1. About 20 feet – the width of the addition.
At that time:
The PP-2 connection to a original ground rod was disconnected.
It does not look like the neutral and ground bus were separated in PP-2.
No ground conductor was installed with the 4 wire feeder.
This is the existing condition now that has been in place for many years.
PP-2 is what the panelboard is currently labeled even though it was originally installed before PP-1.
This has come up because we are adding another panelboard for a new small addition that was to be connected to PP-2.
The question – should something be done for the PP-2 grounding?
It looks like panelboard PP-2 was the original main service panelboard. At some later date an addition was built and PP-2 became a subpanel (with a new feeder) connected to PP-1 which is at the service. The feeder is in a RGS conduit underground to PP-1. About 20 feet – the width of the addition.
At that time:
The PP-2 connection to a original ground rod was disconnected.
It does not look like the neutral and ground bus were separated in PP-2.
No ground conductor was installed with the 4 wire feeder.
This is the existing condition now that has been in place for many years.
PP-2 is what the panelboard is currently labeled even though it was originally installed before PP-1.
This has come up because we are adding another panelboard for a new small addition that was to be connected to PP-2.
The question – should something be done for the PP-2 grounding?