Strathead
Senior Member
- Location
- Ocala, Florida, USA
- Occupation
- Electrician/Estimator/Project Manager/Superintendent
Hey everyone. It has been a while. I am out in the field again as a quality manager for a new hospital project, so I don't get to sit at a computer much. Anyway, I have a couple questions that are bugging me.
Actually I will start with how I understood the code, and you can tell me where to find the references or if it is an urban myth. I thought that we could pull a ground through a box if none of the conductors are cut, but if any conductors are cut, the ground must be cut and bonded to the box. I also thought that if we left enough wire to cut and splice in the future, the ground had to be cut and bonded to the box at the time of installation. I think, after searching the code, the last part, at least, is an urban myth. Please if I am correct for any part of this provide me a code reference. Also, where does it state that only one grounding conductor is required in a conduit.
Here is the reason I ask. My EE on the job is claiming to we aren't ok with our installation. We have a gutter above a panel with 5 1 1/4" conduits with multiple #10 wire circuits protected at 20 amps each having a single #10 ground. He says that we don't comply with 517 redundant grounding and that in order to comply we have to pull a grounding conductor sized per 250.122 which he interprets as being sized per the main breaker in the panel.
Please help.
Actually I will start with how I understood the code, and you can tell me where to find the references or if it is an urban myth. I thought that we could pull a ground through a box if none of the conductors are cut, but if any conductors are cut, the ground must be cut and bonded to the box. I also thought that if we left enough wire to cut and splice in the future, the ground had to be cut and bonded to the box at the time of installation. I think, after searching the code, the last part, at least, is an urban myth. Please if I am correct for any part of this provide me a code reference. Also, where does it state that only one grounding conductor is required in a conduit.
Here is the reason I ask. My EE on the job is claiming to we aren't ok with our installation. We have a gutter above a panel with 5 1 1/4" conduits with multiple #10 wire circuits protected at 20 amps each having a single #10 ground. He says that we don't comply with 517 redundant grounding and that in order to comply we have to pull a grounding conductor sized per 250.122 which he interprets as being sized per the main breaker in the panel.
Please help.