Grouch1980
Senior Member
- Location
- New York, NY
Hey guys,
I have several grounding questions, if you can please help...
1) If you see the detail that I copied here, it shows GEC taps on the top connecting to a grounding bus bar, and the GEC's on the bottom connecting to the grounding electrodes. Where I highlighted in red, shouldn't this be a 3/0 copper ground wire as well? To me it doesn't seem to comply with section 250.66(A), where the wire doesn't have to be larger than #6 AWG. Or does it?
2) In the diagram here, this is from the 2017 NEC handbook. The 350 kcmil conductors at the top / line side are the service entrance conductors. The #3 and #3/0 wires tapping from the 350 kcmil conductors, are those considered service entrance conductors as well? or are they called S.E.C. taps? or just S.E.C.'s?
I have several grounding questions, if you can please help...
1) If you see the detail that I copied here, it shows GEC taps on the top connecting to a grounding bus bar, and the GEC's on the bottom connecting to the grounding electrodes. Where I highlighted in red, shouldn't this be a 3/0 copper ground wire as well? To me it doesn't seem to comply with section 250.66(A), where the wire doesn't have to be larger than #6 AWG. Or does it?
2) In the diagram here, this is from the 2017 NEC handbook. The 350 kcmil conductors at the top / line side are the service entrance conductors. The #3 and #3/0 wires tapping from the 350 kcmil conductors, are those considered service entrance conductors as well? or are they called S.E.C. taps? or just S.E.C.'s?