What is the cause of it? Potential the connections or bonding are loose? Lets say reading was 30ohm, then adding 2 more 10ft rods, the reading is now 45 ohm
Did you move the test points between testing with one rod and testing with three? It might be that there is a local area of dirt that is not real conductive where you stuck your test probe.
both, with and without moving, same results (within) increases
Assuming they aren't permanently connected, if you unhook the new rods, does the measurement return to its original value?
What's the chance it reads 4.5? One can only hope.
..unlikely. I have verified it myself. I thought it was weird!
What testing method and equipment are you using?
How far apart are the rods spaced?
Using AEMC 3640. Fall potential Method @ 62ft and 100ft from the rods and probe
And how far apart are the electrodes? You can get interesting anomalies using the FOP method unless your closest test probe is a large number of diameters away from the total area where the electrodes are located.
Wouldn’t you use a larger bonding wire from one ground rod to the next to reduce the ohms? Like using a larger ground rod sometimes, or longer ground rod? Or like how sometimes in a raceway you need a larger ground wire than any of the conductors?
He is measuring resistance between rod(s) and earth. Even a 18 AWG bonding wire between the rods (effectively making them one electrode when reading the combined resistance) is likely to be much lower resistance then rod to earth resistance.Wouldn’t you use a larger bonding wire from one ground rod to the next to reduce the ohms? Like using a larger ground rod sometimes, or longer ground rod? Or like how sometimes in a raceway you need a larger ground wire than any of the conductors?
Can you explain this a little more? thanks!