Grounding Receptacles and Roaming Ground
Will Wire
California: NEC 2020
Electrical Contractor
I’m working at a house wired in the late 50s early 60s that has a ground wire wrapped around the box nail and then goes to another box nail. When I was an apprentice almost 40 years ago, the guy that trained me called this a roaming ground. He said, since the box was grounded, we were allowed to change an ungrounded receptacles to grounded receptacle by installing a ground pig-tail from the box.
Would this ground wire be considered part of the grounding electrode system?
Was this method receptacle replacement once allowed?
Is installing a grounded receptacle this way today ok?
I am aware of NEC section 250.130 and 406.4(D).
Thanks
Is the metal box properly grounded? If so then a self-grounding receptacle or a receptacle with a bonding jumper is permitted.
Never seen that. :unsure:
Never heard that term.
That part is true.
Definitely not; it's part of the equipment grounding system.
Pig-tailing from a (properly-)grounded box, yes; still is.
With above comments considered, sure.
Miyagi have hope for you. :giggle:
Welcome. (y)
Wrapping the EGC around a nail is not a proper way to bond the box today, nor when it was done years ago. I've seen the ground wrapped around a screw on the back of boxes, but that isn't proper either. You would need to either use a threaded hole and add a ground screw, drill and tap a hole for a grounding screw, or use a grounding clip.
The receptacle can be considered bonded, and not require a pigtail, if using a self grounding receptacle, or removing a screw retaining washer on the receptacle screw if the box is metal and surface mounted, and the box is grounded.
In the older codes they started to require metal boxes to be grounded like within 6' feet of a sink or outdoors before there was grounded romex, they allowed the sheath of BX (now type AC cable) be be the equipment ground or you could run a roving ground around to the boxes, this had to be attached with a 10/32 screw, it was allowed to terminate at a metal water pipe.
if you wan some old code references I can look them up.
It can be an issue when a plumber re-pipes part of a old house with PEX but leaves some metallic pipe.
as a ground fault would just energize the pipe.
In an older home renovation I was involved in, the upstairs bath was wired with early NM W/ground to the receptacle, light, and switch, then continued on to the hallway and a bedroom W/O ground. The kitchen lighting circuit was done the same way.