I'm looking for any guidance and NEC references for requirements for grounding of a medium voltage splice box.
Application is MV cables ran in PVC conduit through a metal splice box. There is no individual EGC as part of the circuit as the concentric shieled on the cables are being used as the EGC. The splice made within the box is completely covered by the insulated splice including the cable shield.
My understanding of the NEC is that all splice boxes need to be bonded to the EGC for a path back to source. Since in this case the PVC conduit does not serve as EGC and the cable shield EGC is not accessible under the splice is there another approved means of meeting NEC requirement for box grounding?
It has been suggested that driving a ground rod to local earth and connecting to box will suffice as adequate grounding?
Looking for any input and NEC references that may be helpful here.
Application is MV cables ran in PVC conduit through a metal splice box. There is no individual EGC as part of the circuit as the concentric shieled on the cables are being used as the EGC. The splice made within the box is completely covered by the insulated splice including the cable shield.
My understanding of the NEC is that all splice boxes need to be bonded to the EGC for a path back to source. Since in this case the PVC conduit does not serve as EGC and the cable shield EGC is not accessible under the splice is there another approved means of meeting NEC requirement for box grounding?