I came across a situation where a customer is running a service lateral from a pad mounted x-former to a pedastal containing metering device and a 200A outdoor disconnect. The pedastal is approx. 15 ft. away from the transformer and the disconnect is grounded using two 8ft. ground rods 6 ft apart. The customer has to run a feeder from his disconnect to his house panel which will be a 200a mcb panel approx 300ft. away. My question is do you have to run 4 wire or can you run 3 wire from disconnect to house and ground panel in house according to 250.32. It would make more sense to me to run 3 wire and install new ground rods at house which will be a shorter grounding source to house panel than running 4 wire (4th wire as egc) and relying on ground rods 300ft. away as your grounding means. There will be no potential between the two grounding sources since the 3 wire feeder will be run in pvc pipe. The house water pipe will also be used as a grounding electrode.