I am checking the grounding and bonding connections on some rooftop hvac units, they are 7 1/2 ton commercial units trane, when they were installed, emt was used as egc.
these are 480 3ph units /with gas heat/with non fused disconnect at unit.
min circuit amp 20.8, ocpd 30 brkr
feeeder #10
question :
most likely the conduit installation, installed 20yrs ago has loose fittings on coupling set screws, and locknuts,
the emt used as egc would be compromised, yes? (have high resistance)
unlikely to open the ocpd in the event of a fault,
so, can you resistance test emt? just like you would wire?
what ohm's reading would be acceptable for 50-60' of emt.
how do you resistance test emt?
gar, zog, brainjohn?
pulling in a egc would be costly and time consuming, on 9 units.
thanks
steve