TFT1980
Member
- Location
- New Jersey
- Occupation
- Licensed Electrical Contractor
Hi all, for a 600-amp 208-volt 3 phase service what size GEC is required for a ground ring. The code states in 250.52 (A) (4) not smaller than 2 AWG. I'm pretty sure that according to 250.66 that I need to install a 2/0 copper conductor. Is this correct? Thanks in advance.