tonype
Senior Member
- Location
- New Jersey
That close to the foundation he hit the footer.
This rod is an electrode for the service?
I think you're right. It looks like it's bent some from hitting a solid object like a footer.
Seriously doubt it's a 10' rod.
It's probably already cut to 3' and just poked into the ground. Did you try pulling on it?
I thought 8' gd. rod were supposed to be installed full depth in ground... my guess in this case, installer hit rock and stopped?? Any other comments would be appreciated.
I think the rod may also be placed laterally rather than vertically in ground and then it is called strip/wire grounding and is much longer in length (Minimum 15 meters).
Looks like a second conductor under a split bolt or other connector further up, the rod I think only has one conductor, but sort of looks like two because it is apparently THHN/THWN with the outer nylon jacket trying to come off of it.Looks like you have 2 conductors under one clamp. I don't believe that is compliant either. The wire would also need to be protected from damage, however, I have this type of install many times from years back.
Not that it is relevant to this thread but the rule for rods is 8' in the ground driven vertically. If rock is encountered then the rod may be driven at an angle not to exceed 45°. If the rock(s) prevent the 45° angle then the rod may be placed in a trench at least 30" deep.
No mention of "strip/wire grounding" and the rod doesn't have to be any longer than 8'.
Also not relevant to this thread but they make 1/2" and 5/8" rods. I always use 1/2" because I could not find the requirement for 5/8" in the code. Is there a code for rod thickness?
Also not relevant to this thread but they make 1/2" and 5/8" rods. I always use 1/2" because I could not find the requirement for 5/8" in the code. Is there a code for rod thickness?
Going off memory here, dont feel like double checking right now: I think 1/2 is ok if its a listed ground rod, but must be at least 5/8 if not listed.
250.52(5) Rod and Pipe Electrodes. Rod and pipe electrodesshall not be less than 2.44 m (8 ft) in length and shall
consist of the following materials.
(a) Grounding electrodes of pipe or conduit shall not
be smaller than metric designator 21 (trade size 3 ⁄ 4 ) and,
where of steel, shall have the outer surface galvanized or
otherwise metal-coated for corrosion protection.
(b) Rod-type grounding electrodes of stainless steel
and copper or zinc coated steel shall be at least 15.87 mm
( 5 ⁄ 8 in.) in diameter, unless listed.
Not that it is relevant to this thread but the rule for rods is 8' in the ground driven vertically. If rock is encountered then the rod may be driven at an angle not to exceed 45°. If the rock(s) prevent the 45° angle then the rod may be placed in a trench at least 30" deep.
No mention of "strip/wire grounding" and the rod doesn't have to be any longer than 8'.
The installer mentioned in post#1 was either not aware of the rule you mentioned or he had really installed strip conductor ground as the electrode looks like a strip conductor rather than a rod. JMO.