Submitted for your consideration
We came to an impass at work over this subject. It concerns an electrode installed for an SDS and does it have to be bonded back to the GES created at the service. We agreed to let an NFPA informal interpretation be the tie breaker. Can't say as I agree but it is what it is.
My position is that the electrode is bonded back to the GES via the EGC.
HERE'S THE QUESTIONS I POSED AND THE RESPONSE:
I have a request regarding NFPA 70 - 2002.
A transformer is installed in a large wood frame warehouse. There is not any water piping or building steel available as in 250.30(4). The transformer is required to be grounded. The transformer is grounded to a rod installed to meet the requirements of 250.53(G) and 250.56.
Question:
1. Is it the intent of the Code that this rod be bonded back to the grounding electrode system described in 250.50?
2. If Q1 is yes, is it the intent of the Code that this conductor be a minimum #6 copper and installed in addition to the Equipment Grounding Conductor installed with the primary conductors?
3. IF Q1 is yes and Q2 is no, is it the intent of the Code that any properly sized Equipment Grounding Conductor with the primary conductors serve as the bonding means described in question 1?
4. If Q3 is yes, does the Equipment Grounding Conductor have to meet the requirements in 250.64(E)?
5. If Q1 is yes; Q2 is no and Q3 is no, is it the intent of the Code that the Equipment Grounding Conductor with the primary conductors be equal to or greater than the size required by Code for the Grounding Electrode Conductor grounding the secondary side of the transformer to the ground rod?
NFPA Response:
Question # 1 Yes. In accordance with 250.50 all grounding electrodes present at a building or structure described in 250.52(A)(1) through (A)(6) shall be bonded together including grounding electrodes that are installed in accordance with 250.30(A)(7) Exception No. 1. In addition, 250.58 requires the use of a common grounding electrode for grounding multiple ac systems (could be supplied by utility service(s), separately derived system(s) or a combination of both) that supply a building or structure.
Question # 2: Yes. A bonding jumper installed in accordance with 250.53 shall be used to bond the multiple electrodes together. The equipment grounding conductor of the feeder circuit supplying the transformer cannot be used as the means to accomplish the 250.50 requirement to bond together all grounding electrodes that are present at a building or structure. The bonding jumper(s) used to connect the multiple electrodes together shall be sized in accordance with 250.66 based specific type(s) of grounding electrode(s) that the bonding jumper(s) is being connected to.
Question # 3: No. The equipment grounding conductor is required to be run with the primary circuit conductors to the transformer and connected to the equipment grounding terminals at the point of supply and at the transformer. Bonding jumpers used to connect grounding electrodes together are required to be connected to the electrode in accordance with 250.70 and it is intended that this be a direct connection between the bonding jumper and the grounding electrode and not through the equipment grounding terminal of electrical equipment.
Question # 4: No. See answers above regarding the use of the equipment grounding conductor as a bonding jumper for connecting multiple electrodes together.
Question # 5: No. See answers above regarding the use of the equipment grounding conductor as a bonding jumper for connecting multiple electrodes together.
We came to an impass at work over this subject. It concerns an electrode installed for an SDS and does it have to be bonded back to the GES created at the service. We agreed to let an NFPA informal interpretation be the tie breaker. Can't say as I agree but it is what it is.
My position is that the electrode is bonded back to the GES via the EGC.
HERE'S THE QUESTIONS I POSED AND THE RESPONSE:
I have a request regarding NFPA 70 - 2002.
A transformer is installed in a large wood frame warehouse. There is not any water piping or building steel available as in 250.30(4). The transformer is required to be grounded. The transformer is grounded to a rod installed to meet the requirements of 250.53(G) and 250.56.
Question:
1. Is it the intent of the Code that this rod be bonded back to the grounding electrode system described in 250.50?
2. If Q1 is yes, is it the intent of the Code that this conductor be a minimum #6 copper and installed in addition to the Equipment Grounding Conductor installed with the primary conductors?
3. IF Q1 is yes and Q2 is no, is it the intent of the Code that any properly sized Equipment Grounding Conductor with the primary conductors serve as the bonding means described in question 1?
4. If Q3 is yes, does the Equipment Grounding Conductor have to meet the requirements in 250.64(E)?
5. If Q1 is yes; Q2 is no and Q3 is no, is it the intent of the Code that the Equipment Grounding Conductor with the primary conductors be equal to or greater than the size required by Code for the Grounding Electrode Conductor grounding the secondary side of the transformer to the ground rod?
NFPA Response:
Question # 1 Yes. In accordance with 250.50 all grounding electrodes present at a building or structure described in 250.52(A)(1) through (A)(6) shall be bonded together including grounding electrodes that are installed in accordance with 250.30(A)(7) Exception No. 1. In addition, 250.58 requires the use of a common grounding electrode for grounding multiple ac systems (could be supplied by utility service(s), separately derived system(s) or a combination of both) that supply a building or structure.
Question # 2: Yes. A bonding jumper installed in accordance with 250.53 shall be used to bond the multiple electrodes together. The equipment grounding conductor of the feeder circuit supplying the transformer cannot be used as the means to accomplish the 250.50 requirement to bond together all grounding electrodes that are present at a building or structure. The bonding jumper(s) used to connect the multiple electrodes together shall be sized in accordance with 250.66 based specific type(s) of grounding electrode(s) that the bonding jumper(s) is being connected to.
Question # 3: No. The equipment grounding conductor is required to be run with the primary circuit conductors to the transformer and connected to the equipment grounding terminals at the point of supply and at the transformer. Bonding jumpers used to connect grounding electrodes together are required to be connected to the electrode in accordance with 250.70 and it is intended that this be a direct connection between the bonding jumper and the grounding electrode and not through the equipment grounding terminal of electrical equipment.
Question # 4: No. See answers above regarding the use of the equipment grounding conductor as a bonding jumper for connecting multiple electrodes together.
Question # 5: No. See answers above regarding the use of the equipment grounding conductor as a bonding jumper for connecting multiple electrodes together.