I've got a question about complying with 250.30 grounding of separately derived systems.
I am working on a project replacing several dry-type transformers in a 4-story building. Almost none of the transformers have a grounding electrode conductor installed. To remedy this, I plan on installing a ground bar on each floor with a #3/0 GEC interconnecting them as allowed by 250.30(A)(6) and then providing the required size GEC (per T250.66) from each ground bar to each individual transformer.
(There is no accessible building steel available to ground to. This is a circa 1968 concrete building and everything is covered).
My question is: Does the #3/0 GEC have to connect to the cold water pipe within 5 feet of where it enters the building? The cold water pipe is in a very difficult spot to get to and it has an existing GEC connected to a main grounding bar in the electrical room. Can I connect my #3/0 GEC to the ground bar and be in compliance since the cold water pipe is already bonded?
This is a project on a state-owned building. The state reviewer made a comment about bonding the hot water piping also. I'm kind of at a loss there and would love some feedback on that too.
I am working on a project replacing several dry-type transformers in a 4-story building. Almost none of the transformers have a grounding electrode conductor installed. To remedy this, I plan on installing a ground bar on each floor with a #3/0 GEC interconnecting them as allowed by 250.30(A)(6) and then providing the required size GEC (per T250.66) from each ground bar to each individual transformer.
(There is no accessible building steel available to ground to. This is a circa 1968 concrete building and everything is covered).
My question is: Does the #3/0 GEC have to connect to the cold water pipe within 5 feet of where it enters the building? The cold water pipe is in a very difficult spot to get to and it has an existing GEC connected to a main grounding bar in the electrical room. Can I connect my #3/0 GEC to the ground bar and be in compliance since the cold water pipe is already bonded?
This is a project on a state-owned building. The state reviewer made a comment about bonding the hot water piping also. I'm kind of at a loss there and would love some feedback on that too.