Ok so I have looked everywhere to find the actual verbiage on this. So the ground rod to the newly installed or even existing XFMR or separately derived system cannot really be used unless there is no water or steel electrode? Now I guess what I am asking is that the EI wanted me to bring the grounding electrode conductor back to the main grounding electrode system. The only thing I see is for the water or steel per 250.30 (A) (7) that requires either of the 2 however I do see 250.50 that requires these to all be bonded together. So is that where the EI gets that it has to go back to the main grounding electrode system? For example: Existing grocery store with new switchboard, and some new XFMRs installed. Would each one of these XFMRs be required to go back to the main grounding electrode system where the new switchboard is? There is no building steel. And do we really rely on water given that most services dont have 10' of copper in the ground? Im just having a hard time understanding the electrode for the separately derived system going all the way back to the main grounding system. Thanks