memyselfandI
Senior Member
- Location
- Hampton Roads, Virginia
According to art 250.30(a)(3), the GEC shall connect the grounded conductor of the derived system to the grounding electrode as stated in 250.30(a)(7). When you run an equipment ground with the primary you bond it to the casing of the trnsformer. From the secondary side, is it acceptable to run a wire from the casing through XO to a ground rod driven next to the transformer? Building steel and cold water lines are available, but they are not close to the transformer. This application has me concerned. Will the equipment ground be sufficient to satisfy the grounding of the derived system(which is the same size as the secondary), or does the re need to be a seperate wire for the derived system to groungd the secondary side of the transformer. IMO the ground rod is not tied the grounding electrode system and therefore is not a grounding electrode. 250.50 says that they all need to be bonded together to form the ground electrode. Thoughts would be greatly appreciated