I am a home inspector, not an electrician. I was an electrical apprentice for a year.
Anyway. I was inspectiong a house yesterday and saw a set-up I am not familiar with. The outside of the service looks like this. See photo
http://www.miproperty.com/indigo/electric outside5.JPG
Two #6 stranded copper ground wires come out of the exterior disconnect below the meter. One wire goes to a ground rod outside and the other goes to the water meter.
http://www.miproperty.com/indigo/electricoutside2.JPG
The water meter is properly bonded
http://www.miproperty.com/indigo/electric meter bonded .JPG
The inside service panel does NOT have a #6 copper gound to it. Some of the 12-2 and some of the 14-4 are twisted up which looks a little like #6 but.....I looked very closely. No ground in the panel.
http://www.miproperty.com/indigo/electricservice11.JPG
Question is.....This couldn't be correct, could it????????
See all photos of electric here.
http://www.miproperty.com/indigo/
Anyway. I was inspectiong a house yesterday and saw a set-up I am not familiar with. The outside of the service looks like this. See photo
http://www.miproperty.com/indigo/electric outside5.JPG
Two #6 stranded copper ground wires come out of the exterior disconnect below the meter. One wire goes to a ground rod outside and the other goes to the water meter.
http://www.miproperty.com/indigo/electricoutside2.JPG
The water meter is properly bonded
http://www.miproperty.com/indigo/electric meter bonded .JPG
The inside service panel does NOT have a #6 copper gound to it. Some of the 12-2 and some of the 14-4 are twisted up which looks a little like #6 but.....I looked very closely. No ground in the panel.
http://www.miproperty.com/indigo/electricservice11.JPG
Question is.....This couldn't be correct, could it????????