christlike
Member
- Location
- cleveland, OH, USA
[FONT=wf_segoe-ui_normal]Hey mike can u shed some light on Table 250.66? Does the table refer to residential, commercial, and industrial? Does it refer to the primary grounding: metal underground water pipe, or does this table refer to the supplemental electrode system? Even though I know full well how to interpret the table in conjuction with table 310.15 B 7 dwelling service conductor sizes, I have a dillema I ran #6 copper wire from the hot, cold, and gas back to the 200 amp dwelling service panel is this legal according to 250.66 (A) "grounding electrode conductor shall not be required to be larger than 6 awg copper ". Does 250.66(A) connections to Rod, pipe, or plates electrodes refer to the supplemental grounding? So not to confuse any more, my question is basically this: for a 200 amp dwelling service do I go with a size 4 copper grounding electrode (according to table)conductor for the 2 driven ground rods or is it for the cold water meter/ hot water tank closet hot, cold, and gas? And where am I allowed to use the size 6 copper wire then according to the exceptions of 250.66 (A) [/FONT]