grounding terminations in panelboards

Status
Not open for further replies.

ndc81167

Member
does anyone know of any code reference that requires only manufactures listed grounding lugs for the panelboard being installed
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
does anyone know of any code reference that requires only manufactures listed grounding lugs for the panelboard being installed

I agree with Trevor but I don't know anything that would make you use the manufacturers ground lug. If the holes are tapped and the number of threads (250.8(A)) are maintained then why not. I have seen single lugs added to panels.
 

iwire

Moderator
Staff member
Location
Massachusetts
I agree with Trevor and Dennis.

Should be no problem but if the panelboard label specifies a grounding bar kit (which they all seem to) I can see an inspector pulling the 110.3(B) card.
 