bilbo336
Member
- Location
- Durango, CO
Article 250.24(C) states that "Where an ac system operating at less than 1000 volts is grounded at any point, the grounded conductor(s) shall be routed with the ungrounded conductors to each service disconnecting means and shall be connected to each disconnecting means grounded conductor(s) terminal or bus." The NEC Handbook says that if you have a grounded system the grounded conductor must be run from the service transformer neutral bus to the SE disconnecting means neutral bus and bonded to the grounding electrode, whether you use the neutral or not. We commonly design 3 wire 480V service entrances to switchgear or MCCs and do not use the neutral. If we need single phase voltages we install a transformer to handle the single phase loads. My question is can the "grounded conductor" from the transformer to the SE equipment be an uninsulated wire? So far, I have not found a requirement to use an insulated one and I have a contractor that installed an uninsulated equipment ground wire along with the three phase conductors.