Your questions are cryptic and poorly worded, can you clarify? For a grounding transformer, the 125% overload applies. So, continuous operation over 125% is not allowed. However, a grounding transformer is intended to supply a lot of current during a fault elsewhere on the distribution system, as such, the OCPD must be delayed to permit the grounding transformer to do its job. A MCB with magnetic protection may have a problem allowing the short term fault current. An electronic LSI breaker has the same issue unless the settings are correctly set so that downstream breakers have time to operate at the current sourced by the grounding transformer. A full system model and study is needed.