A 480vac, 3 phase circuit, consisting of three ungrounded conductors and an equipment grounding conductor, is run to supply a machine in an industrial plant.
At the machine, the circuit is tapped onto to supply a small single phase transformer with a 120vac secondary. This transformer supplies a duplex receptacle for limited loads (e.g. radio, fan.) The transfomer is a two winding transformer, so there is no direct electrical connection between the primary and secondary (it is not an autotransformer.) The secondary circuit is protected by a fuse in one conductor.
I contend that this secondary circuit fits the definition of a "seperately derived system" and that the conductor that is not fused needs to be grounded.
Further, if the transformer is 1000VA, or less, the secondary can be considered to be a class 1 control circuit and it is sufficient to bond the grounded conductor to the metal frame or enclosure of the transformer. The equipment grounding conductor of the secondary circuit is also connectecd to the transformer frame or enclosure.
However, if the transformer is greater than 1000VA a seperate grounding electrode conductor must be run to a suitable grounding electrode (e.g. nearby metal water pipe, effectively grounded building steel, etc.) The equipment grounding conductor of the transformer's supply circuit may not be used to ground the grounded conductor of the transformer secondary.
Is this a correct interpretation of the code rules?
At the machine, the circuit is tapped onto to supply a small single phase transformer with a 120vac secondary. This transformer supplies a duplex receptacle for limited loads (e.g. radio, fan.) The transfomer is a two winding transformer, so there is no direct electrical connection between the primary and secondary (it is not an autotransformer.) The secondary circuit is protected by a fuse in one conductor.
I contend that this secondary circuit fits the definition of a "seperately derived system" and that the conductor that is not fused needs to be grounded.
Further, if the transformer is 1000VA, or less, the secondary can be considered to be a class 1 control circuit and it is sufficient to bond the grounded conductor to the metal frame or enclosure of the transformer. The equipment grounding conductor of the secondary circuit is also connectecd to the transformer frame or enclosure.
However, if the transformer is greater than 1000VA a seperate grounding electrode conductor must be run to a suitable grounding electrode (e.g. nearby metal water pipe, effectively grounded building steel, etc.) The equipment grounding conductor of the transformer's supply circuit may not be used to ground the grounded conductor of the transformer secondary.
Is this a correct interpretation of the code rules?