Re: Grounding Transformer sizing
Here?s some things to consider:
Which voltage needs the ground bank? 138 kV or 34.5?
If it is 138 kV, look at using the neutral of the step up transformer with a single phase grounding transformer or reactor. If its 34.5 kV, select the type of grounding transformer: zig-zag, wye-broken delta, high-resistance grounded wye, or other?
What is the allowable or required ground fault current from the bank or from the other generators and loads on the system?
What is the time rating? If the fault is supposed to clear in 3 seconds, can you use a transformer with a 10 second rating? Per IEEE Std- 32 "Test Procedure for Neutral Grounding Devices", a grounding transformer's continuous rating is 3% of its 10 second rating. A 1200 kVA transformer can handle a 40 MVA fault current for 10 seconds. (1200 kVA = 40 MVA x 3%)
The transformer's time rating and KVA may also depend on the type and speed of the primary and backup relaying.
A good reference is Lew Blackburn?s ?Protective Relaying?. He has a chapter on grounding and grounding transformers.
Good Luck
What is the time rating needed? If the fault is supposed to clear in 3 seconds, can you use a transformer with a 10 second rating. Per IEEE Std- 32 "Test Procedure for Neutral Grounding Devices", a grounding transformer's continuous rating is 3% of its 10 second rating. A 1200 kVA transfomrer could handle a 40 MVA fault current for 10 seconds.
The transformer's time rating and KVA may also depend on the type and speed of the primary and backup relaying.