If a transformer supplies a 120/240v, single phase, 200amp panelboard from a 480v, 3 phase supply and if the secondary ungrounded conductors from the transformer to the panleboard are sized 3/0 awg copper. This transformer is near the service disconnect to the building and it is grounded to the metal underground water pipe. The min. size copper grounding electrode conductor permitted for this transformer installation is:
For this problem would I refer to Table 250.122 and would 6 awg be correct?