Looking at a job today at a TV station. They are having problems with grounds.
They have a 225kva transformer 480 / 120-208 3 phase that feeds the MDP in the same room. In the MDP they have five - 200amp feeders installed in EMT all 3 phase 4 wire going to panels in there computer room. The computer room has six cable trays over the computers. The GEC for the transformer goes to a copper plate on the wall and from this plate the GEC goes to building steel. Also from this plate six bonding/grounding wires go to the six cable trays and four wires go to four panels and are terminated on an IG ground bar. In the fifth panel they have an IG bar with the ground wire going to building steel. On the cable tray they used MC cable to wire IG receptacles when they found out that they could not use MC cable for IG receptacles the original contractor came back and installed a ground lug and a wire in the panel and landed it on a lug on the cable tray. He told them that now all the boxes would be grounded.
I told them that the IG wire should be run from XO in the transformer to the MDP and then installed with the feeders to the panels. I also told them the MC could not be used for IG receptacles and that they should replace the wire.
I would like to know if the bonding/ground wires on the copper plate to the cable trays is OK? I consider the wires to be bonding wires.Thanks for any input you guy's have.
They have a 225kva transformer 480 / 120-208 3 phase that feeds the MDP in the same room. In the MDP they have five - 200amp feeders installed in EMT all 3 phase 4 wire going to panels in there computer room. The computer room has six cable trays over the computers. The GEC for the transformer goes to a copper plate on the wall and from this plate the GEC goes to building steel. Also from this plate six bonding/grounding wires go to the six cable trays and four wires go to four panels and are terminated on an IG ground bar. In the fifth panel they have an IG bar with the ground wire going to building steel. On the cable tray they used MC cable to wire IG receptacles when they found out that they could not use MC cable for IG receptacles the original contractor came back and installed a ground lug and a wire in the panel and landed it on a lug on the cable tray. He told them that now all the boxes would be grounded.
I told them that the IG wire should be run from XO in the transformer to the MDP and then installed with the feeders to the panels. I also told them the MC could not be used for IG receptacles and that they should replace the wire.
I would like to know if the bonding/ground wires on the copper plate to the cable trays is OK? I consider the wires to be bonding wires.Thanks for any input you guy's have.