I am wondering if the bonding jumper to a grounding terminal on the receptacle is required or am I still permitted to omit it in cases of self grounding receptacles.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I am wondering if the bonding jumper to a grounding terminal on the receptacle is required or am I still permitted to omit it in cases of self grounding receptacles.


Self grounding receptacles install to a properly grounded box do not need a jumper to the box--260.146. Here is an example where neither the self ground or jumper is required

(B) Contact Devices or Yokes. Contact devices or yokes designed
and listed as self-grounding shall be permitted in conjunction
with the supporting screws to establish the grounding
circuit between the device yoke and flush-type boxes.

ry%3D400
 

kwired

Electron manager
Location
NE Nebraska
Doesnt this violate the Section in 406 requiring the grounding terminal to be connected to the EGC?

I didn't read through requirements to get exact wording, but the metal box is also required to be bonded to the EGC, so all three - box, receptacle, and EGC are bonded together.
 

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
Doesnt this violate the Section in 406 requiring the grounding terminal to be connected to the EGC?

Bonding does not necessarily mean a "conductor". it can be via a screw, conductor, strap....

So, if you have a metallic conduit, metallic box with metallic raised cover then you don't need a wire jumper between receptacle and the metallic box.

If you have all metallic with a metallic plaster ring then you need a jumper between the receptacle and the box or a self grounding receptacle.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I would add with surface mounted boxes (1900 or 4 11/16") and finished covers there are two styles of cover, one with dimpled edges and ones without. The dimpled edge covers do not require a bonding jumper between the receptacle and the metal box. The non-dimpled covers do.
 

fmtjfw

Senior Member
SORRY IT'S A CIRCLE

SORRY IT'S A CIRCLE

here is the handbook

ry%3D400

If that illustration is from the "Handbook" in connection with grounding receptacles using a mounting screw, then it just reenforces why I avoid the "Handbook".

An isolated ground receptacle (denoted by the triangle) has no connection between the yoke and the grounding pins

Grump, Grump, Grump!!! :thumbsdown:

Never mind, it is a hospital grade receptacle that just happens to be orange.
 