Is it still Permissible to omit a receptacle bonding jumper under certain conditions?
Can you be a little more specific with the question?
Roger
I am wondering if the bonding jumper to a grounding terminal on the receptacle is required or am I still permitted to omit it in cases of self grounding receptacles.
(B) Contact Devices or Yokes. Contact devices or yokes designed
and listed as self-grounding shall be permitted in conjunction
with the supporting screws to establish the grounding
circuit between the device yoke and flush-type boxes.
Doesnt this violate the Section in 406 requiring the grounding terminal to be connected to the EGC?
Doesnt this violate the Section in 406 requiring the grounding terminal to be connected to the EGC?
here is the handbook