grounding wire size

Status
Not open for further replies.

df3557

Member
I am going to run 3-#3 THHN and a #8 THHN for my grounding wire for a single phase 100a sub-panel in the same structure as the main panel . The supply house thought I should a #6 as did my father-in-law who has been an electrical contractor for 40 yrs. They are probably right but when I read table 250.122 it sure looks like it would be #8. I would appreciate it if someone could clear this up for me.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I agree with Bryan, but I'm curious as to why the others thought that a #6 is required?
 