250.140 Frames of Ranges and Clothes Dryers
Frames of electric ranges, wall-mounted ovens, counter-mounted
cooking units, clothes dryers, and outlet or junction boxes that
are part of the circuit for these appliances shall be connected to
the equipment grounding conductor in the manner specified by
250.134 or 250.138.
Exception: For existing branch-circuit installations only where
an equipment grounding conductor is not present in the outlet or
junction box, the frames of electric ranges, wall-mounted ovens,
counter-mounted cooking units, clothes dryers, and outlet or
junction boxes that are part of the circuit for these appliances
shall be permitted to be connected to the grounded circuit conductor
if all the following conditions are met.
(1) The supply circuit is 120/240-volt, single-phase, 3-wire;
or 208Y/120-volt derived from a 3-phase, 4-wire, wye connected
system.
(2) The grounded conductor is not smaller than 10 AWG copper
or 8 AWG aluminum.
(3) The grounded conductor is insulated, or the grounded
conductor is uninsulated and part of a Type SE service entrance
cable and the branch circuit originates at the
service equipment.
(4) Grounding contacts of receptacles furnished as part of the
equipment are bonded to the equipment.