Re: grounding wires
It is common practice and NEC compliant to run multiple circuits through a conduit using a single equipment grounding conductor (sized to the largest circuit).
Once you get to a pull/splice box these circuits usually go off in multiple directions; at this point additional equipment grounding conductors are added to each raceway to follow the circuit conductors. These additional EGC are all spliced together in the pull/splice box to the original 'home run' EGC.
Why is it common practice (and code compliant) to splice 1/2 dozen EGC together in the splice box for the home run, yet once you get to the distribution panel it is suddenly 'bad practice', 'not good workmanship' to splice EGC's together as Z-men is inquiring about?
The NEC Handbook has a commentary about splicing EGC's together (for the single home run) indicating they are not concerned about upsizing this conductor because multiple faults are unlikely to occur.
BTW - I too prefer providing additional terminal blocks in the panel when I need extra spaces for the EGC's. Personally, I do not splice EGC's together in the panel, but I do not have a problem with others doing this.