grounding with emt

Status
Not open for further replies.

wireday

Senior Member
Location
New England
Occupation
Master electrician
OK to run EMT raceway, pull a ground wire and pass through 4 squares to receptacle without connecting EGC to 4 squares,only connected to receptacle? if not could you reference article, thanks
 
See 250.148
Basically if they simply pass thru with no splice or termination, then no connection to the box is needed.
 
OK to run EMT raceway, pull a ground wire and pass through 4 squares to receptacle without connecting EGC to 4 squares,only connected to receptacle? if not could you reference article, thanks
Doesn't the non-required EGC, one pulled in, need to terminate to any box where the associated line conductors are terminated, say on a receptacle, regardless of whether it also terminates on said receptacle?
 