The attached spec means you have a wire from each grounding bushing AND THER IS A LUG ON THE BOX that the wires attach to?
 

Attachments

  • Capture.JPG
    Capture.JPG
    23.5 KB · Views: 0

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
You would have to provide a termination lug(s) in the box. You will have to provide lug(s) suitable for the connection of four grounding conductors, one from each grounding bushing and one from each conduit.

If the EGC in the raceway it equal to or larger than the specified bonding jumper between the grounding bushing and the box, you could land the internal EGC on the grounding bushing and continue that same conductor to the termination on the box.

A couple of notes to the above after re-reading the question.

If they are using the raceway as the EGC, there would be no EGC in the conduit. If there is an EGC in the raceways, and if the ungrounded conductors pass through the box without a splice or termination, the EGC would also be permitted to pass through the box without being terminated.
 